Elevator Forum

Indirtwetrust
@indirtwetrust
Noble Member
Joined: Jan 1, 2010
Topics: 63 / Replies: 1696
Reply

This is for a GCS Attachments Screen Shot 2023-08-30 at 3.32.14 PM.png (193.32 KB, 55 downloads)

3 years ago
Reply

Check your 24v at DZ1 and DZ2 in the controller. There’s a lot of voltage drop possible in that circuit. You want to adjust the power supply so you ha...

3 years ago
Reply

No LON involved on a simplex TAC22 unless you have LON PIs. That’s when you’ll see a single yellow or blue port in IMS. You have to have at least 1 LO...

3 years ago
Reply

It says more than 4096, move the bottom directional limit down a hair and run it again.

3 years ago
Reply

I think I’d try another CLC

3 years ago
Reply

I don’t think any software will let you save a scan if the first floor is below 4096 but you get a 25-01 fault and wouldn’t be able to get the car to ...

3 years ago
Reply

So couple things on the TKE telescopic jacks.The runby and bottom overtravel are critical for it to work correctly. Minimum bottom overtravel is 8-1/2...

3 years ago
Reply

So this is kind of confusing but what the car means to say is that it’s on “Viscosity Overtemp Shutdown” not heat up the oil “Viscosity.” I think it w...

3 years ago
Reply

You know there are 2 different versions right? Original MOVFRs have an RJ-45 jack and use a PU usually made by Mitsubishi. Then the MOVFRIIs have an R...

3 years ago
Reply

Sounds like your parameter unit isn’t communicating with the inverter. Just need to determine which one is the issue (or the cable.) Plug your PU into...

3 years ago
Reply

It’s NEC code to ground all raceway…. And besides the safety reasons, which are serious, grounding is critical with modern communication protocols to ...

3 years ago
Reply

Group adjustment LBY sets lobby floor, that’s where it’ll park.Group adjustment LER sets # of cars requested to lobby.I don’t think you can put a dela...

3 years ago
Reply

TPS is a fault flag on the View Hoistway F3 Screen. Equates to Position error at UNTx/DNTx. You want to make sure all the NTS/ETS switches are in the ...

3 years ago
Reply

Increasing the brake pick voltage is not going to help hold 125%… Adjusting the air gap as tight as possible might. It’s also really important on thos...

3 years ago
Reply

When I started in construction there were always jobs that went into 7 12s for a month or so at a time. We were young and ate it up.

3 years ago