For the TAC 20 there’s another board that goes in the COP to convert the TAC20’s 485 comm to CAN for the Wittur CAN adapter board. And most likely wil...

3 years ago
Reply

Still pretty low though. Like I said, I max the open and close watchdog timers out on those. One maxes at 20 and the other at 25.

3 years ago
Reply

What’s DOP set to?

3 years ago
Reply

No, you just need to add the IOs and make D12=2 (D13 for rear) If you have port/con7 or 8 available you need 6 IOs DO, DO1, DC, DCN, DOL, DCL. DO1 is ...

3 years ago
Reply

Those are just Tac32s right? You definitely can manually add discrete IOs for an MOVFR and change the door type parameter.Or sell an LD-16 linear upgr...

3 years ago
Reply

This is pretty normal on a TAC50 if they’re running manual speed but you didn’t say that so I assumed they’re running full speed. For the slow doors n...

3 years ago
Reply

Man I’d put a data logger on it or at least set a couple traps in the safety circuit

3 years ago
Reply

Ya that should be fine, just wire it like the picture.

3 years ago
Reply

That’s what’s marked as factory wires on the drawing. The Siemens starters come with that wired up already. What I did leave off that print though is ...

3 years ago
Reply

On a DMC, inspection is only relay logic. There’s nothing the CPU can do to prevent the car from running on inspection so you’re missing something. If...

3 years ago
Reply

Absolutely the toggle switch. Depending on which pole fails you can get all kinds of weird issues. Losing P24C can cause various selector lockups, P24...

3 years ago
Reply

What kind of controller is the upcoming Mod?As far as I know all the Tac32s use the CAN expansion board but also have TKE’s software in them. You coul...

3 years ago
Reply

This is a kit that makes a 211 a Hydrofit. Replaces the IOBD with a Hydro Accel IOBD and a GCS CPU. It’s cool they have that option since the 211 IOBD...

3 years ago
Reply

That’s Viscosity, heating up the oil. Probably not related to your 2802 fault. For that you should check your down NTS magnets on the back of the tape...

3 years ago
Reply

Sounds like your software is old and doesn’t support the parameters over 48, that’s fine. You need to set the correct number of floors then do a hoist...

3 years ago