Topic starter   [#35822]
Hey all

I just took over a GEN2 job and the car to lobby switch at the lobby panel is not operating. Switch rings out fine, it appears to be set up, but the building insists its never worked. Does this have to be activated by a parameter? I can not find anything in manuals. Any info would help.



   
Quote
(@neville)
Eminent Member
Joined: 17 years ago
Posts: 24
 
Yes. The key has to be connected to a RSL card. Set the address on the RSL to the one assigned for CTL and enable CTL in the logic board to 1



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@neville)
Eminent Member
Joined: 17 years ago
Posts: 24
 
Yes.So set the DIP switches on RSL card to 1290. Then enable CTL using the service tool. Then set CTL-P to the floor you want the lift to return to.



   
ReplyQuote
(@neville)
Eminent Member
Joined: 17 years ago
Posts: 24
 
Yes.So set the DIP switches on RSL card to 1290. Then enable CTL using the service tool. Then set CTL-P to the floor you want the lift to return to.
Attachments
CTL Parameters.png (193.32 KB, 36 downloads)

Last edited by Neville; 08/31/23 07:48 AM. Reason: Added file


   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
But you don’t set the dip switches to 1290. You find an extra input on an existing RSL card or add an RSL card then address it to an unused port. Then in 1-3-2 you enter 1290 and enter the address your input is at. 4 inputs and 4 outputs at each port.



   
ReplyQuote
(@neville)
Eminent Member
Joined: 17 years ago
Posts: 24

   
ReplyQuote
(@steveb)
Active Member
Joined: 17 years ago
Posts: 15
Topic starter  
Thanks for the quick response.

I am pretty green to Otis equipment. Does each lift have an RSL card at the lobby panel?

My lobby panel has a car to lobby switch for each car. It is a 3 position spring loaded switch: car to lobby, 0 (neutral pos.), and park.



   
ReplyQuote
(@neville)
Eminent Member
Joined: 17 years ago
Posts: 24
 
Steve. Your CTL switch must be connected to an a RSL CARD INPUT.

When the key switch is turned on, it will give the signal to the RSL.

Check the address on the RSL seeing which links are on on which are off. The binary code will be 1 2 4 8 16.So seeing which pins are on you can come to know the address on the RSL.

Then this address and the input pin number you set for the address 1290 on the controller. For example

If links 123 are on, in the RSL, then the address will be 7. And if you have used input number 1 to connect the CTL switch to the then the address is 07/1. So input this on 1290.

Hope this helps. I stopped working since 2008, so my apologies for the incorrect info in my previous post which was corrected by another member. All the best.



   
ReplyQuote
(@steveb)
Active Member
Joined: 17 years ago
Posts: 15
Topic starter  
Not a problem Neville! Thanks for the help. Glad I am finally able to get my hands on some of this OTIS stuff.



   
ReplyQuote
(@neville)
Eminent Member
Joined: 17 years ago
Posts: 24

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
What kind of RSL card is in the lobby panel? Are all 3 cars on the same board? What are its dip switches set to? And if you want to let us know exactly where the switches wire to we could tell you more specifically what to enter on the tool. Are these 311 Gen 2s or GCS Gen 2s? Are there labeled indicator lights in the lobby panel that will have to be addressed too for car to lobby and park?

Last edited by Indirtwetrust; 09/02/23 02:50 PM.


   
ReplyQuote
(@steveb)
Active Member
Joined: 17 years ago
Posts: 15
Topic starter  
GEN 2 GCS

IT LOOKS LIKE EACH CAR HAS A SWITCH GOING TO AN RS-5 CARD

6 dip switches

1 and 2 are down the other four are up.



   
ReplyQuote
(@steveb)
Active Member
Joined: 17 years ago
Posts: 15
Topic starter  
Okay so I believe for an RS5 I’ll have 4 inputs and outputs.

Dip switches give me an address of 60 -

If I identify what input the switch is on, let’s say it’s on E5

Then I’m looking at 60/5 for 1290…



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
E5 is input 1 on the RS5 card so 1290 would be 60 1