Once you resolve the matter please let us know Steve

3 years ago
Reply

I am happy it is resolved. Thank you for the feedback.

3 years ago
Reply

Check the parameter EN-BCD. Most probably it is set to 1. Set it to O.Please advise if this resolves the issue.

3 years ago
Reply

Steve. Your CTL switch must be connected to an a RSL CARD INPUT.When the key switch is turned on, it will give the signal to the RSL.Check the address...

3 years ago
Reply

Thank you Jadam. Truly appreciated 🙏🙏🙏🙏

3 years ago
Reply

Yes you are right. Thank you for the correction

3 years ago
Reply

Like other brands, does Orona do a reset for 0 floor when it reaches the Ground Floor?If cat top switch is in inspection, will indicator display - - o...

3 years ago
Reply

3.2.5 Failures related to EMERGENCY POWER OPERATION (EPO)<M> <1> <2> <1> <GO ON> EPO shutd. Event number:0101Car is shut...

3 years ago
Reply

Which brand of lift and which model is it?

3 years ago
Reply

Yes.So set the DIP switches on RSL card to 1290. Then enable CTL using the service tool. Then set CTL-P to the floor you want the lift to return to. ...

3 years ago
Reply

Yes.So set the DIP switches on RSL card to 1290. Then enable CTL using the service tool. Then set CTL-P to the floor you want the lift to return to.

3 years ago
Reply

Please check whether Test run mode is active

3 years ago
Reply

Yes. The key has to be connected to a RSL card. Set the address on the RSL to the one assigned for CTL and enable CTL in the logic board to 1

3 years ago
Reply

Please ensure the encoder wires are routed separately from brake wires and motor wires or any other wires.How many meters rise is the lift and does it...

3 years ago