Check the rubber tire on the tach gen. The when it wears down it won't make good contact with the sheave. I think that would give you a 2009 sub code.

10 years ago
Reply

What is the sub code for the 108?

10 years ago
Reply

Caps are usually in the top right corner of the controller, they're about 1" dia. X 5" long, usually blue. The diodes are in the operator to make the ...

10 years ago
Reply

Just sent you something. First check the caps in the controller! Should be 2 uf caps in series. Common failure that blows fuses, and not always immedi...

10 years ago
Reply

MOD?

10 years ago
Reply

First I would make sure MC1 contacts are good and not reading more than an ohm or so. Make sure motor windings don't read to ground and choke isn't op...

10 years ago
Reply

You can get Hyperterminal for free too. I've tried Putty, Teraterm but had better results with Coolterm. Hyperterminal though is the only program that...

10 years ago
Reply

Most TIVs do have software that you can use IMS with. It does not disable Hyperterminal on its own, only if the CPU has been updated to a JC5 will Hyp...

10 years ago
Reply

Is this a 10K Quantum drive? Regen? Can you get the 2407MC to reset and attempt to run or does the red LED never go off?

10 years ago
Reply

It should be HA N/O contact 3/5 or, HAT N/O contact 6/4

10 years ago
Reply

Right on! Thank you.

10 years ago
Topic
Replies: 3
Views: 4286
Reply

If this is an MG set without tach feedback I'd say it's under compounded but I've never seen one of these controllers either. Is inspect speed close u...

10 years ago
Reply

Have you put your eyes on the switch itself to make sure it is resetting fully every time?

10 years ago
Reply

I also have as a possible cause:"Run Circuit (XO6) was sent low but IN remained high.Defective wiring in inspection circuitDefective CLC"I've never se...

10 years ago