Tac 5004 1863, 658 fault

7 Posts
3 Users
0 Reactions
6,129 Views
(@take-the-stairs)
Estimable Member
Joined: 17 years ago
Posts: 120

   
Quote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729

   
ReplyQuote
(@take-the-stairs)
Estimable Member
Joined: 17 years ago
Posts: 120

   
ReplyQuote
(@take-the-stairs)
Estimable Member
Joined: 17 years ago
Posts: 120
Topic starter  
Still having a 658 fault went through my drive jumpers on all boards to no avail. It's not motor wiring! It may be drive set up? Any help?



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Is this a 10K Quantum drive? Regen? Can you get the 2407MC to reset and attempt to run or does the red LED never go off?



   
ReplyQuote
(@take-the-stairs)
Estimable Member
Joined: 17 years ago
Posts: 120
Topic starter  
yes its a Quantum, it will reset, and i try to run it on insp. 658 pops up causing sometimes
a rrf reset, or the red light on the drive to be reset. always resets goes back to normal.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
First I would make sure MC1 contacts are good and not reading more than an ohm or so. Make sure motor windings don't read to ground and choke isn't open or something. Check very carefully for something that may have come unplugged or disturbed while you were in there like the LEMs. Make sure the IGBT plugs are not pushed all the way on the pins.

It isn't uncommon though to loose another component at the same time as an IGBT, especially the Inverter Interface Cards. At this point I would go through the Universal Drive Testing Procedure. Unfortunately, unless you work for TKE you are not going to have the tester. I can send you the tester manual but you will only be able to do the more basic tests.



   
ReplyQuote