Ya, it’s great. It’s just some buttons in series with the ribbon cable to fire the IGBTs independently. Maybe someone should make a copy.

5 years ago
Reply

The universal drive tester is made by ITS so I don’t think you can buy it from Vertical Express

5 years ago
Reply

I found on the newer logic boards they stopped putting the cap on the boards so now I just pull them off.

5 years ago
Reply

Those position faults are likely from a power cycle. Common with the BP inputs over LON. TAC20s will drop MCC1 to turn off the starter with certain fa...

5 years ago
Reply

Ya, since you found the actual problem, I’d put all the old boards back in

5 years ago
Reply

2nd that, their videos are excellent. With an I2, my money would be on the lowering or check valve seats. These valves are super easy to pull apart an...

5 years ago
Reply

Not TAC20, it’s a TAC20-03. Try a GET command.

5 years ago
Reply

That’s a TAC20-03. If the GET doesn’t clear it up you’ll probably have to replace the CPU. You could try re-loading the software if you had a backup b...

5 years ago
Reply

It shouldn’t need it since it’s not actually doing anything but I found an old note that this fixed some odd syncing problems. It’s possible this was ...

5 years ago
Reply

Add it

5 years ago
Reply

You do have BLO in your IO map right? It should be port 8 bit 2.

5 years ago
Reply

If the original CPUA is still functional you can download the software right out of it and upload it to the new board. If it’s dead and there is no US...

5 years ago
Reply

You need to do an FJR to make sure the car can do a proper resync. You shouldn’t be getting a low pressure fault on a resync unless something is wrong...

5 years ago
Reply

Don’t know, probably

5 years ago
Reply

LD-03 DOL, DCL. sensors in header, magnets on hanger connecting bracket. Item 14, 15, 16. Attachments Screen Shot 2021-07-28 at 5.48.48 PM.png (260...