Tac 32. Fault 1110

29 Posts
9 Users
0 Reactions
21.2 K Views
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
So Maintentaice in the building had been recycling power every time b4 I got there until today. Now I have a 2nd code. 1074 jack resync low pressure. I removed the buffer springs to see if that will stop it from happening for now. Magnets on back of tape are fine.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
You need to do an FJR to make sure the car can do a proper resync. You shouldn’t be getting a low pressure fault on a resync unless something is wrong.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Fault code is 1074. In manual it says pressure switch active .
On the UIT is says 1074 jack resync low pressure shut down .
I manually re sync it and it leveled up fine after



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
It seems the problem is my jack low pressure switch .. I wonder if my up leveling strainer is causing this.

Last edited by Jluff; 07/30/21 11:44 AM.


   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Update. Every time car gets sunk in pit i get 24v to prsw . Causing shutdown. Car still levels fine after sync and shuts down level at bottom terminal landing... car passes standing test ...There is no visible leaks anywhere. System is dry .. my car is not bottoming out .. has anybody else had this problem ?

Last edited by Jluff; 07/31/21 03:23 PM.


   
ReplyQuote
(@silly)
Estimable Member
Joined: 17 years ago
Posts: 215
 
Depending on software, older versions would spit the 1074 out, as a proper resync does allow PRSW to come active. IDWT has the right idea, do a FJR on a clean slate and see what faults pop up. The 1074 could just be a ghost, and not part of your problems. While resyncing, verify you do not come off NTSB or DLT. That's where my money is right now, as while syncing, you lose placement, car won't make an effort to "find" itself, but on a power cycle it will...

As for the original door issue, potentially car could have been racking during the resync, allowing a car door or hoistway door to open, causing that original 1110. Again easy to duplicate by using the FJR.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Did a FJR and got 1074 and 1110 .. also turned power off and manually lowered car into pit. Turned power on and got same results. 1074 and 1110 as car leveled up out of pit. With prsw jumped out it does not give me any faults during resync forced or manually lowered

Last edited by Jluff; 08/01/21 10:06 AM.


   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
It shouldn’t need it since it’s not actually doing anything but I found an old note that this fixed some odd syncing problems. It’s possible this was fixed with a software update too. What version is the software?



   