I have an elevator stuck on this status. Fire hat on in the car. Will not reset. Have changed all boards and cables. Still will not reset. Any ideas?
17/08/2021 10:07 am
Maybe try to find where the JNFF input is on the car board, and try different NC or NO connections on it?
Also, have you checked your 24vdc is not dropping too low?
Last edited by heisenberg; 08/17/21 02:09 AM.
Topic starter
17/08/2021 11:18 am
Ok. I will check it. 24v is good. Sitting around 27v
17/08/2021 9:40 pm
Originally Posted by Jblack83
I have an elevator stuck on this status. Fire hat on in the car. Will not reset. Have changed all boards and cables. Still will not reset. Any ideas?
I would be curious to know what "all boards" you changed?
17/08/2021 9:43 pm
I've seen this as well as controller hung up on other different status/states and 9 times out of 10 a quick 5 min drain of the 360 cap fixes it everytime(gotta clear the RAM)
Topic starter
18/08/2021 4:03 am
Have tried draining the cap. Did not work. Have replaced the GCI360, CRIP, CFIRE, CIOACD, CPBHNA and the cables that link the CFIRE, CPBHNA and CIOACD.
I found an old tech article from Schindler back in 2007. There was a version that was produced for about 5 months that had a programming glitch that would not allow phase 2 to reset. Most of these were found on warranty recall. However this elevator is that vintage and shortly after install the building went empty and sat dormant for a decade. A work around was moving it on inspection to a floor other than the main egress landing and releasing it. In theory according to the article it should recall on phase 1 and shut off phase 2..
We will see headed there today to try it
I found an old tech article from Schindler back in 2007. There was a version that was produced for about 5 months that had a programming glitch that would not allow phase 2 to reset. Most of these were found on warranty recall. However this elevator is that vintage and shortly after install the building went empty and sat dormant for a decade. A work around was moving it on inspection to a floor other than the main egress landing and releasing it. In theory according to the article it should recall on phase 1 and shut off phase 2..
We will see headed there today to try it
Topic starter
18/08/2021 5:01 am
Nope.. Didn't work. Any other ideas anyone?
Topic starter
18/08/2021 5:11 am
All out of Ideas. I guess I will just have to loose the contract and have them call Schindler. Heart breaking because I may never know what the issue was.
18/08/2021 8:15 am
I have one that will not reset phase 1 unless key switch is reset then double reset the controller
18/08/2021 9:05 am
I had a 400a that wouldn't come off fire recall. Turned out I had a bad hall call board. Only the elevator gods know why. Got to love that Schindler product.
18/08/2021 9:24 am
Have you connected Cadi to it?? To see all node statuses
18/08/2021 7:19 pm
Definitely don’t rule out any of the boards you have already swapped. A significant percentage of the boards I’ve got from Schindler have been bad out of the box.
20/08/2021 12:47 am
Ya, since you found the actual problem, I’d put all the old boards back in
07/12/2021 4:47 am
Does anybody know what was the solution for the JNFF issue?
Topic starter
07/01/2022 5:46 am
Yes. 2 of the CIO boards I swapped straight out of the box were bad.