Were the parameters recorded or did you have to go through the book and set them 1 by 1? Just wondering if you’re sure on the Valid opening parameters...

5 years ago
Reply

So if you’re on auto it will take a car call, go to the floor it not open the door? Or I’ll it just not open for hall calls? Simplex or in a group? Wh...

5 years ago
Reply

Originally Posted by Jluff How does the suppressor wire in to a plug in relay ? You wire it across the coil

5 years ago
Reply

Only if the one that’s in there is too small. The suppressor Print number is 381AF1. Should cross to a part number.

5 years ago
Reply

Contactor would be a good guess.

5 years ago
Reply

You have to connect to the controller with Blue IMS then open drive Smartfast. If the table fills out it’s communicating. The UIT is great because you...

5 years ago
Reply

I’m not sure how the 1009 could be related to the 1040. But for the 1009, it could be the starter logic board picking MUTS when it shouldn’t or there ...

5 years ago
Reply

I think that’s an ESCO controller. Does it have a funky selector?

5 years ago
Reply

What he said, and while this depends somewhat on what type of valve you’re working on, I don’t know how you could let a car run without checking the d...

5 years ago
Reply

If they’re 10K drives, set M109 to 0

5 years ago
Reply

I think the only move here is to put a 3 phase power quality analyzer on it. If it’s building power it’s not your problem. If it isn’t building power ...

5 years ago
Reply

That’s a TAC50-04 then, bad VM on a TAC50 card rack gives unexplained 56 faults because it drops the 15v supply to the drive/DSP. TAC50-04 VM cuts AC1...

5 years ago
Reply

DB9-5 to Con6-1DB9-2 to Con6-2DB9-7 to Con6-3DB9-3 to Con6-4

5 years ago
Reply

What was the fire service issue?

5 years ago
Reply

Bad normally closed contact on the Delta contactor, MC or PMC

5 years ago