Hello. I’m getting a 1030 then a 1009 (Init SD down)
Very intermittent. However I think I witnessed it once. It’s a 4 stop and it seems to happen at the top floor. The door opens. Then closes a few inches and the indicator goes blank and doors lose power. Then all of a sudden it comes back to life and doors close and it goes down.
Very intermittent. However I think I witnessed it once. It’s a 4 stop and it seems to happen at the top floor. The door opens. Then closes a few inches and the indicator goes blank and doors lose power. Then all of a sudden it comes back to life and doors close and it goes down.
1009 - valve contact error. (MCD open ) down run failure, valves or MC not ready. MCD inactive or MCE active during down run
. Defective MCD input
. Defective MCE input
. Defective relays
1030- Leveling sequence error - Leveling inputs activated in an invalid sequence.
Any ideas Would be appreciated.
Do I need lon cable to change input ports? Don’t have one
I have old IMS
17/03/2022 5:18 am
Have you tried replacing all the valve control and mcc relays?
17/03/2022 10:15 am
Be sure the retainer clips are on all the relays. It's also worth noting the finder and schrack relays seem to have different thickness pins, can't remember which ones are thicker, but one relays will fit looser than the other. I went on an OT callback that the car was shutdown because one of the relays literally halfway fell out of its base, the mechanic had just swapped all the relays out and threw the retainer clips away.
Topic starter
17/03/2022 9:39 pm
I did replace mcc relays. Then I ran out. Ordering more That’s interesting about the different relays. I don’t even know which ones I have .. I think there are clear schracks on bottom row then blue ones above.
18/03/2022 3:29 am
The finder ones were trouble back in the day
25/03/2022 7:23 pm
Originally Posted by lowoil
The finder ones were trouble back in the day
If i remember correctly the orignal Finder relays only had contacts that were rated for 6Amps. Now they are rated for 8 amps. This increased the life of the relay and made them more reliable
Topic starter
30/03/2022 7:29 pm
This happened again .. took a few weeks. This time it was 1040 first then 1009. Lots of relays were changed few weeks ago. Seems to be people get trapped. But it’s always running wheh I arrive. Any ideas what to focus on ?
Topic starter
31/03/2022 5:33 am
If I have a bad MCE OR MCD input. How do I change them ?
31/03/2022 7:15 am
I’m not sure how the 1009 could be related to the 1040. But for the 1009, it could be the starter logic board picking MUTS when it shouldn’t or there is supposed to be a certain suppressor on the MUTS relay. Should be the cylindrical thing in black heat shrink with black wires coming out. Not one of the plug in ones. The starters can bleed through quite a bit through up to speed and that relay will chatter and even fail to drop after a run.
Topic starter
31/03/2022 4:20 pm
Txs dirt. Do you have a part number for the suppressor.
Also noticed my main line comtactor is humming very loud
Also noticed my main line comtactor is humming very loud
Last edited by Jluff; 03/31/22 08:29 AM.
Topic starter
01/04/2022 9:16 am
Would a bigger starter help ?
02/04/2022 7:27 am
Only if the one that’s in there is too small.
The suppressor Print number is 381AF1. Should cross to a part number.
The suppressor Print number is 381AF1. Should cross to a part number.
Topic starter
02/04/2022 7:45 am
How does the suppressor wire in to a plug in relay ?
02/04/2022 9:29 pm
If 1030 was your first fault at the top of the hoistway check the magnets at the back of the tape , make sure that they are in the proper sequence
02/04/2022 10:56 pm
Originally Posted by Jluff
How does the suppressor wire in to a plug in relay ?
You wire it across the coil