Lost all programming on the original board.

Used our tool, was able to get it functioning, but Fire Service doesn’t work correctly. Was told that we would need a new board and chipset to correct.

Ordered a new board and chipset, programmed for a 3 stop and reset selector top to bottom.

Car will only run between 1 & 2. Ignores 3rd landing altogether.

Any help would be greatly appreciated.

A quick note, we have put the original board back in, reprogrammed and it runs fine to all landings but still has Fire Service problem.

Only issue is with the new boards.

Last edited by Lav8rMEn; 03/02/22 07:21 PM. Reason: Additional information


   
Quote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
Change the parameter that controls the type of FireSercice that you want. On new board, set floor tables correctly to tell the unit it has three floors.



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
What was the fire service issue?



   