03/03/2022 1:30 am
Hey guys,
Anyone have answers to lowering/removing extreme static discharge when hotel guests hit the call buttons on the upper floors (floors 2-4) of a hotel? The elevator landing area as well as the corridors have carpet and in the winter months, it really gives a big static charge when guests hit the call buttons. It doesn't happen/not near as prevalent on the first floor as it's all tile in that area. We have one TKE Endura 35 II A and one TKE Endura 25 A MRL Hydraulic TAC32 elevators with standard stainless steel trim and stainless steel call buttons at each floor.
Anyone have answers to lowering/removing extreme static discharge when hotel guests hit the call buttons on the upper floors (floors 2-4) of a hotel? The elevator landing area as well as the corridors have carpet and in the winter months, it really gives a big static charge when guests hit the call buttons. It doesn't happen/not near as prevalent on the first floor as it's all tile in that area. We have one TKE Endura 35 II A and one TKE Endura 25 A MRL Hydraulic TAC32 elevators with standard stainless steel trim and stainless steel call buttons at each floor.
03/03/2022 4:43 am
You could ground every hall station to the building steel, or switch the buttons out with plastic ones, but they suck, had a problem like that years ago, we just grounded them to the duct work which was attached to the building steel
03/03/2022 5:27 am
Grounding won't help. The faceplates and boxes should already be grounded. I think the biggest problem with static is low humidity. You might ask the maintenance if any thing could be done. I have the same problem in the wintertime in my own house.
04/03/2022 7:13 am
Another option that is commonly used on bronze buttons to prevent oxidization is a clear insulating conformal coating on the buttons.
04/03/2022 7:16 am
Might also want to apply to face plate as the static is discharging to ground. Ask your service mechanic.
05/03/2022 8:51 pm
Unless the hall station is low voltage, you should not isolate it from ground.
06/03/2022 2:40 am
Had to add additional grounding on 2 jobs because I kept losing hnb cards with carpeted floors. Fixtures were bonded to the box only. This was mentioned by tech support after everything else was eliminated. Lost 2 cards in one week once. Problem went away after.
06/03/2022 11:07 am
Had the same problem , asked the customer to get the carpet sprayed with anti- static spray , it definitely helped