Did you enter all parameters correctly. You have to Validate proper front and rear floors.

11 years ago
Reply

Type, Year, Traction, Hydro?

11 years ago
Forum
Reply

+1 to that. Double reboot on inspection should do the trick. Check out this topic.the original host/forums/ubbthreads.php?ubb=showflat&Number=1507...

11 years ago
Reply

I have had a TAC 20 do that and it was a bad door board. Like it was loosing communication. Replaced the door board and no more problem. How do you ge...

11 years ago
Reply

JP2 jumper must be off on a TAC 20. But I'm not sure on a 32. Never done it before.

11 years ago
Reply

You have to have Lon talk adapter to bind nodes. Yes, IMS/Advanced Lon Manager.

11 years ago
Reply

PM sent.

11 years ago
Reply

Usually a bad selector board.

11 years ago
Reply

That's one of the worst I've seen. I'd love that contract. Replace the 2 O-rings and clean the screen on each and make mega bank. And they would notic...

11 years ago
Reply

LN board in COP. Try to just Bind Nodes but you might have to replace LN, and L24 boards in COP.

11 years ago
Reply

Does it have LON?

11 years ago
Reply

Yea, I said WTF to his post. I thought your post was hilarious. Are there any admins here to get rid of these people?

11 years ago
Reply

WTF?

11 years ago
Reply

If software chip is fried then you will not have LED on either. Just had that happen.

11 years ago
Reply

Its the JP2 Jumper, on the IOD card. TAC 32 doesn't use the EBAD and EGOOD. Although they are on the board, I think.

11 years ago