You can right lick in the IO map to toggle between metered logic and positive logic to change how some IOs are displayed to you in IMS. You can also i...

3 years ago
Reply

I suggest the FT-10 USB adapter so you aren’t tied to an ancient laptop.

3 years ago
Reply

You have to restart the computer after switching to 485 and it has to be a real serial port, no USB converters.

3 years ago
Reply

Not really. If you have 1 empty discrete port you can add the 7 CLO inputs and the SOA enable in the group on that port and make S10=3. Or just add th...

3 years ago
Reply

You need to load a LON config

3 years ago
Reply

I would expect then that you’d get the same fault if the car tried to run up or level up. For some reason you aren’t getting a run command to the star...

3 years ago
Reply

No

3 years ago
Reply

To remove viscosity you just lift the wire for OLTS

3 years ago
Reply

No LON on a TAC32. Just do a TECC after you power it up with the new CWIL board.

3 years ago
Reply

What’s not right though is that TS1/TS2 is connected directly to CLU, jumping out the top terminal slowdown switch.

3 years ago
Reply

Much better to get the correct config from someone at TK.

3 years ago
Reply

Ya there’s no LON on a TAC20-03

3 years ago
Reply

Not a good idea… the jobs and some of the IO positions aren’t standardized.

3 years ago
Reply

You select the group in the control panel and open the IO map (control + I)

3 years ago
Reply

No, I’ve never seen a product that converts the DMC’s particular 485 comm to discrete IO for an MOVFR or any other discrete operator. It’d be a great ...

3 years ago