It worked for me but it was like 10 years ago

2 years ago
Reply

I once had this problem on an 411 and just copying them to new chips fixed it.

2 years ago
Reply

I would definitely try replacing the Schrack relays with Finder. Part# 50.12.9.024.1000. RS Online has them (formerly Allied Electronics) RS Stock# 71...

2 years ago
Reply

LE output is on the CLC. You’d have 24vdc at LE on the relay board in the machine room T11-10. You’d pretty much need 24vdc there for the car to level...

2 years ago
Reply

I’m not sure about CHS but it’s pretty strange that the car would level back in on inspection. I would guess maybe it doesn’t know it’s on inspection,...

2 years ago
Reply

Is your new CLC a BP4 but the original is not? In this case the old software would not be compatible and you wouldn’t get a WD. All that’s needed to g...

2 years ago
Reply

If this is an un-adjusted job file, every will have to be setup from scratch including fire service parameters. SAF3 is the drive so won’t even run on...

2 years ago
Reply

You can’t use Hyperterminal on the 32 bit. What you’re seeing is it going into Z-modem and seeing no USB stick then leaving Z modem and flashing fast ...

2 years ago
Reply

When you’re checking to see if you have voltage to the input, make sure you read right across the IO, not using VC from the terminal strip for common....

2 years ago
Reply

I agree that they just have to leave it for you so you can fix it. As for the replacement relays, I’d suggest you order the actual IBM 4 poles from Ve...

2 years ago
Reply

I haven’t heard that we’re supposed to be going back and adding this to all IMC-AC controllers but I have done a few of these wiring change kits on IM...

2 years ago
Reply

There’s also an optocoupler array and a Darlington pair driver chip on the Motion board that fire Wye, Delta, UP, & UPX. Separate Opto and transis...

2 years ago
Reply

With 1 riser and 2 cars you have to setup car 1 with car 2 off, build the LON tree, name nodes, find & bind. Then turn car 1 off and do the same f...

2 years ago
Reply

No it’s not in the manual but something that happens sometimes is the UIT won’t work after loading the correct job file. The solution is to load anoth...

2 years ago
Reply

When you have a car fault it’s best to look at the display that shows the fault/warning bits and see which is high. I sent a PM yesterday.

2 years ago