I will be installing a new CPUA board 6300xE1 tomorrow on an Tac50-04 and was curious if I need to upload new software to the board. If so what is the process for that? The current job file USB stick is missing….
Topic starter
19/09/2024 1:05 am
Can not get the controller on Z modem, anyone run into this issue?
19/09/2024 1:27 am
Make sure you’re pressing and holding RST. While holding RST, press and hold UDL. Let go of RST and continue to hold UDL until STAT LED displays Z-modem blink. If it doesn’t go into Z-modem may be bad CPUA board. Is WD LED lit? Do you have 1.5, 3.3 & 5VDC? Is the 3V coin cell battery good? It’s possible the board may be completely unprogrammed with no software whatsoever. Also the software files you’re trying to install need to be in a folder labeled update inside a folder labeled tke - all lower case.
Topic starter
19/09/2024 1:41 am
Yes to all of that…. This is a brand new CPUA 6300xE1 from vertical Exspress. There is no software in it. Battery is good, voltage everywhere is good. When I use the RST & UDL procedure it never blinks like it’s supposed to, it blinks very fast and the UIT never says ZModem. The software is in a usb stick on my computer and I’m trying to get the controller on Z modem so that I can upload via hyper terminal….
19/09/2024 2:17 am
You can’t use Hyperterminal on the 32 bit. What you’re seeing is it going into Z-modem and seeing no USB stick then leaving Z modem and flashing fast to indicate there’s no job file in the CPUA. You have to have a USB stick 8gb or less with a tke folder in the root. In the tke folder make a folder called update and put the generic file and the job file in there ( job file should be .cfg) then with the USB stick plugged directly into the CPUA put it into Z modem. You’ll see the flash rate you’re looking for while it loads. If successful you’ll get a solid WD. For some reason new boards don’t like to take both files the first time so if it comes up flashing fast again, put it in Z-modem one more time. If the job file went through it won’t be in the update folder anymore.
Topic starter
19/09/2024 3:39 am
Lord have mercy… it took 7,8,9 times I lost count before it finally took the files. It’s alive now but floor tables are missing. Attempting to do a hoistway can, D26=1, car is stopped and on auto but still rejects the scan. Safe 3.4, & 5 are not up and the only fault I’m getting is 1056: “Floor tables of encoder counts not set up when attempting an auto run. Not on inspection and the level reference in Non Volatile memory for any floor is valid…”
19/09/2024 7:12 am
If this is an un-adjusted job file, every will have to be setup from scratch including fire service parameters. SAF3 is the drive so won’t even run on inspection until the drive is happy.