Reply

Do you have the adjuster prints from the manual? With them Its fairly straightforward to put a meter on the outputs and and see if they’re working or ...

2 years ago
Reply

Just to be clear, is reopen firing to open the doors or could the door be being pulled off the limit then the controller re-opens the door so door tim...

2 years ago
Reply

You just rename it _07c000.dat. It’s good practice to make another copy named _0f8000.dat and load them together with the 3 generic files. You can loa...

2 years ago
Reply

Sorry I should’ve said they’re in the group

2 years ago
Reply

Like I said earlier, don’t use V6R12 if you have FL_ floor lockouts or the car will be chasing phantom calls. I had to roll back to V6R10 on a ton of ...

2 years ago
Reply

That comes from guys putting things like checked starter connections on their tickets after a MAX call was generated that included a 1529. The system ...

2 years ago
Reply

Every time I’ve found a DMC on EPO there’s been a blown fuse on the relay board. Don’t remember which one.

2 years ago
Reply

The 1529 is NOT a Siemens starter fault. It’s a fault for a traction car that says it lost CAN comm with the drive. The starter is not a drive and doe...

2 years ago
Reply

For Tac20 set LER to 1 and LBY to park floor. For a duplex if you want both to park there, LER=2

2 years ago
Reply

I sent you some thing. You’ll want to put the CAN termination jumpers (or resistors for a 6300PA3) on the door board on and the jumpers on the AAR boa...

2 years ago
Reply

If whoever built the LON tree originally didn’t do an upload to the controller you won’t be able to see anything in LON Explorer. The tree will have t...

2 years ago
Reply

I think that jumper must be in the wrong position. It’s the only reason I can think of that it would be happy with 1 less port than is actually there....

2 years ago
Reply

If you open LON Explorer and select the LN card, are there the same number of ports as you have L24 cards in the SPI loop? Because the test for the SP...

2 years ago
Reply

With a null modem cable or adapter

2 years ago
Reply

The first part all sounds like power supply. You said it tested okay but you need 5.1 vdc to the CLC card and virtually no AC on it. Now that you’ve r...

2 years ago