The motor contactor failed to Energize (MCD/MCE)
MCD is Active, or MCE is Inactive After a Run
Possible Causes:
A defective MCD input
A defective MCE input
A defective MC contact
Defective relays
Possible Solutions:
Verify the starting current on the solid state starter
I have never had to just replace the cpu only in a running tac 20 with lon, so I'm not 100 percent sure that i am correct. I have built a tac 20 tester from scratch and added software,config files, then used lon adapter to program new ln boards. maybe i will try to just remove the cpu and put in a new one and see if the ln boards will still work with just the cpu replaced. any thyssen guys have the absolute answer? thanks
NOTE: When the Advanced LON Manager opens the adapter, but does not communicate with any node.
1. CLOSE IMS if opened!
2. INSTALL LONWORKS
3. REBOOT
4. Open the Control Panel from the Start Menu.
5. Open LonWorks� Plug 'n Play (ONLY PLUG AND PLAY)from the Control Panel .
NOTE: If LonWorks Plug 'n Play is not an available option, the drivers for the LonTalk card will need to be installed.
6. From the LonWorks Plug 'n Play window, left-click the pull down arrow under NI Application .
NOTE: PCC10NVI is the program default setting, every time it is installed.
7. A list of options will appear under the NI Application box. Left-click NSIPCC
8. After NSIPCC appears in the NI Application box, left click APPLY in the LonWorks Plug 'n Play box.
9. Click the Diagnostics button (the Diagnostics window will open).
10. Click the Comm button, and then click the YES button.
11. Click the OK button, and then click the YES button.
12. Click Ok Button.
13. Open IMS, Open advanced lon manager
The adapter should now be operational.