I’ve got a DMC1 with doors cycling normal speed every 20, or so, sec with no demand..

Car runs perfectly when demand placed, no delay, close limit is made at closed position

Any tips?
Thank you



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@elevator-logic)
Trusted Member
Joined: 17 years ago
Posts: 37
 
DMC doors cycle if it thinks a hoistway door is open at a floor it isn't at. I would clean all HW door interlocks and see if the problem goes away. Also it could have a bad curtain/Safe Edge.



   
ReplyQuote
(@lowoil)
Reputable Member
Joined: 17 years ago
Posts: 270

   
ReplyQuote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635
 
1) Built up junk on door tracks at locked position.
2) Linkage from operator to car door needs looked at for loose bolts on driving arms.
3) Shorting SE or PHE cable
4) Broken limit collar...or maladjusted limits.
5) Door belt deformed on the motor sheave at full closed position.
6) Door belt walking off of big sheave near closed position.

All common stuff, but #1 is common on Dover.