Dmc door board

28 Posts
12 Users
0 Reactions
37.1 K Views
(@whadafack)
Trusted Member
Joined: 17 years ago
Posts: 80
 
Make sure your replacing it with a 6300py4 board. Install the capacitor in the controller on p150 and g150. Replace all the belts. If they are dry-rotted or too tight or loose it will throw the counts off. Make sure the door close and open limits make. Good luck



   
ReplyQuote
(@street-rodder)
Eminent Member
Joined: 17 years ago
Posts: 25
 
Well if your CLC is an old version the new door board won't communicate with it, then you have to upgrade all the boards.



   
ReplyQuote
(@beaupeep)
Honorable Member
Joined: 17 years ago
Posts: 316
Topic starter  
Ok, i've replaced motor, encoder, belts, door board. It's practically a new door op and i'm still getting a 65000 pulse count. Anyone have any other ideas



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@beaupeep)
Honorable Member
Joined: 17 years ago
Posts: 316

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
You got me. Sure sounds like you have a digital encoder on it. Did you say what part # board you are using? Is there any AC on the 12vdc from the power supply?



   
ReplyQuote
(@beaupeep)
Honorable Member
Joined: 17 years ago
Posts: 316
Topic starter  
It's the optical encoder that comes with the motor. Is there 2 different types? I only see one on vert express.



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
The optical one is correct, it's the big black plastic case with 2 switches inside and a notched wheel. There is a small digital encoder for the PA door boards that's 500 cpr. You can get that motor with either encoder on it.



   
ReplyQuote
(@beaupeep)
Honorable Member
Joined: 17 years ago
Posts: 316

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
J1 is on for front doors. J2 reverses the hand of the doors, if they run open when you press MDC you change J2. I don't remember what J3 is for but it should be off. J4 is off unless you have an EH board and need more torque.

Last edited by Indirtwetrust; 05/24/16 11:36 PM.


   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Are you getting door faults? Like a 309 phasing fault? You must have a 307 if the saved count is more than 1280 counts.



   
ReplyQuote