20/04/2016 8:41 am
Make sure your replacing it with a 6300py4 board. Install the capacitor in the controller on p150 and g150. Replace all the belts. If they are dry-rotted or too tight or loose it will throw the counts off. Make sure the door close and open limits make. Good luck
26/04/2016 11:32 am
Well if your CLC is an old version the new door board won't communicate with it, then you have to upgrade all the boards.
Topic starter
21/05/2016 4:31 am
Ok, i've replaced motor, encoder, belts, door board. It's practically a new door op and i'm still getting a 65000 pulse count. Anyone have any other ideas
21/05/2016 9:10 am
Do you get a different count if you move a limit?
Topic starter
21/05/2016 11:42 am
Yes, it gets higher
21/05/2016 11:29 pm
You got me. Sure sounds like you have a digital encoder on it. Did you say what part # board you are using? Is there any AC on the 12vdc from the power supply?
Topic starter
22/05/2016 5:44 am
It's the optical encoder that comes with the motor. Is there 2 different types? I only see one on vert express.
22/05/2016 11:06 am
The optical one is correct, it's the big black plastic case with 2 switches inside and a notched wheel. There is a small digital encoder for the PA door boards that's 500 cpr. You can get that motor with either encoder on it.
Topic starter
25/05/2016 7:00 am
What do the jumpers do the door op board
25/05/2016 7:36 am
J1 is on for front doors. J2 reverses the hand of the doors, if they run open when you press MDC you change J2. I don't remember what J3 is for but it should be off. J4 is off unless you have an EH board and need more torque.
Last edited by Indirtwetrust; 05/24/16 11:36 PM.
25/05/2016 7:56 am
Are you getting door faults? Like a 309 phasing fault? You must have a 307 if the saved count is more than 1280 counts.
Topic starter
25/05/2016 9:13 am
Nope, it won't let me save
28/07/2016 6:43 am
Did you resolve the problem?