1964 Otis.. Had on oil and grease for 9 years went to do the five year test and it would not lift the load. Left it alone due to more pressing issue's. Three weeks later it is shut down, the gov electrical switch has tripped in the up direction only. Ohm out everything and find one of the fields is open in the hoist motor. Replace it and then it will not level in the down direction without adjusting the neutral on the generator brushes. At this point it is still overspeeding in the up direction. Go through all the contacts, fingers, resistors again and decide the last option is to replace the generator.
As you can guess by this post it is still doing basically the same thing.
We are going to have to eat a lot on this one and that's ok in the end. I have to get the customer going.
Any ideas.
I will post a picture of the print.
Agree, that I think there may still be an issue with the motor fields, or at least some genny fields(the burning out of a motor field may have taken out others in the circuit). Have you another lift that is working to measure fields? I would check the ohms of each motor field coil disconnected( it may be unbalanced), plus the intercoils, and do the same with shunt field of the generator. The print is a little hard to see, but the GSEF( I think- above the armature loop circuit) I would check, plus the direction field(cant see what its called) on the left hand side, but should be the generator shunt field. Check for ohms, shorts to earth, for balance between up and down etc. Adjust the neutral plane to the mark on the generator and you shouldn't have to move this. Any way let us know how you go.
Going back today. The speeds are 200fpm car. Up was 270 and down was 180. Gen type 63 GA 125 volts 18 amps. rpm 1800
108-b157052b
This idea is a good one. Also I have found that its a good idea not to get too technical from the start, as you can go around in circles. Is this a single car or in a bank? If more than 1 lift, I would check the ohms of the motor fields( as they burned out), then the same for the generator fields( shunt field, levelling field etc), then the resistance tubes(are these lift the ones with the dials?). Then compare this to another lift, which can give you a snapshot of the tuning from lift to lift, which may eliminate/or find an issue you may be having. Also I see that your lift is over speeding in the up direction by 70 fpm, and I seem to remember(rightly or wrongly) that tuners used to want a slightly less fpm in the up direction than the down, purely to eliminate the possibility of over speeding occurring due to the counterweight pulling the car down. Measure your speeds, chocking out 1E etc, as you may find which speed is out of whack. Also I would make sure that your not getting a very small short to earth on up main contactors which can also give you a out of compounding effect, however unlikely.