108-2009 = Torque feedforwards are not tuned, torque limit is too low, speed controller is not tuned, problem with motor speed feedback or wrong syste...

2 years ago
Reply

AT400?

2 years ago
Reply

Door time close protection.. Check for mechanical bind, bearings, crack in cam, bad contacts etc simply removing power and restoring will reset this

2 years ago
Reply

What is bionic 7, USA?

2 years ago
Reply

Check 61u cigar switch for 75 LCE can't see front side floor control board in floor 1 for 1401

2 years ago
Reply

Which code are you referencing?

2 years ago
Reply

Is it a tan Yaskawa drive?

2 years ago
Reply

Sorry I got ahead of myself, I thought we were talking about a CRIP board on a 330A!

2 years ago
Reply

0445 E_DRIVE_TRIP_PREPARATION_FAILUREThis section describes the 0400_0499_DRIVE error E_DRIVE_TRIP_PREPARATION_FAILURE.The drive trip preparation wasn...

2 years ago
Reply

Sounds like the relays are failing on the board, if you get the board repaired see if the company will socket the base so if this happens again you ca...

2 years ago
Reply

Have you tried adding friction modifier? Also I cannot remember the technical term but there is a square galvanized rail that needs to be lubricated a...

2 years ago
Reply

Pm me your email

2 years ago
Reply

55503922 - have you tried that Part # ?I have a spare parts manual for 3300 I can send you if that helps

2 years ago
Reply

That sounds right, I wouldn’t really trust anything not oem with Schindler equipment.

2 years ago
Reply

PM your email