Do you have an email address, so I might be able to help you?

3 years ago
Reply

Ok but check the other things and maybe use Ivmon to see if the fault is in the drive unit

3 years ago
Reply

What was the error before changing the board?How old is the Nvram... Also check all the can connectionsE9 NET NOT WORKING- There is something wrong wi...

3 years ago
Reply

sftail = Start failIts normal tachometer fail.. Check that the tachometer scaling jumper is in the correct position on the control board 385:A1

3 years ago
Reply

Arca 2 whit omron drive..

3 years ago
Reply

What kind of diagnostic machine are you using? arca 1 and arca 2 are not the same connector, if it is not the right connector you can lay the canbus d...

3 years ago
Reply

what version of ims?

3 years ago
Reply

Modus works to Arca 1 and 2 but not for 3. But you can do most things without the usb plug

3 years ago
Reply

Main contactor in drive fails to pick but start permit does change, Main contactor and Start permit input picked and dropped for 3 times

3 years ago
Reply

Lce operating system right? If it is with the new EN 81-20 standard and the light curtain fails, it may well do this. If can't close the door, it will...

3 years ago
Reply

On the option board you set J9 to front ore Rear, The opt board has 8 input. If you need some dokument just write 🙂

3 years ago
Reply

Hi If it is an LCE controller, you must check your 61:u sensor (error 72) you should probably make a new shaft setup, menu 5-2-1 (error 83)

4 years ago
Reply

In the hand terminal https://www.youtube.com/watch?v=V3rDvjCxJCA

4 years ago
Reply
4 years ago
Reply

I have tried something similar, the sensor might become active on the bolt joints.Turn off the shaft light and look at B30 or 30 when you run the insp...

4 years ago