Was the gen pulled or rewired or anything? Or did it just stop working?

9 years ago
Reply

Ya I wish I knew what the RPM was supposed to be set to. I usually just upload a profile with Hyperterminal. You will lose operation from the manual b...

9 years ago
Reply

That's a 1/6th hp D.C. Motor for a linear operator. Set DCM to 1, LDO to 1, LHO to 1 for a left hand door and 0 for right hand, set RPM correctly. Thi...

9 years ago
Reply

So you had a PA2 and put in a PA7 right? If you have a 1/6 HP motor it should bea PA6, PA7 is for the 1/2 HP motors but I think it should work anyway....

9 years ago
Reply

The TAC50-04 manual is all I use for Synergy. There are specific Synergy manuals but there really isn't anything else in there that's useful. No secti...

9 years ago
Reply

Probably not software... what fault(s)? 681? 10K drive or Accord? Synergy or PM motor?

9 years ago
Reply

Is it a TAC50-04 or a 32T?

9 years ago
Reply

Do yourself a big favor, get a thumb drive and backup the job!

9 years ago
Reply

I would call MCE

9 years ago
Reply

Most likely not getting MCE input when car tries to run up. Up to speed contact on starter has to close and pick MUTS relay, MUTS picks MCE input.

9 years ago
Reply

I don't think I was clear on "matching" the car and group IOs. A better way to say it is the IO maps have to "Line up." There will only be a few IOs i...

9 years ago
Reply

Ok so I have a 188E on my coffee table jumped out so it thinks it's on Auto and tries to take hall calls. This works:S10=9, S19=1 this puts car on sec...

9 years ago
Reply

I found it! DLO_ for down hall call override and ULO_ for up hall call override. Awesome thank you! I also see FLO_ for floor lockout override, maybe ...

9 years ago
Reply

So I see you can set CS5-13 or activate an HCLA input to enable hall call lockout. Would you use HLO_ for override inputs? As recently as 2 months ago...

9 years ago
Reply

That's fine for car call security but I am not aware of any IO that can be added to lock out hall calls on a TAC20. FL inputs were only added for 32 b...

9 years ago