Elevator Forum

Indirtwetrust
@indirtwetrust
Noble Member
Joined: Jan 1, 2010
Topics: 63 / Replies: 1696
Topic
Replies: 3
Views: 2922
Topic
Replies: 0
Views: 1757
Reply

I was thinking maybe someone ran a backup scan while the bad battery was pulling the voltage down to 4v.

7 years ago
Reply

Snubbers are suppressors. They’ll be wired from each input to VC on the controller terminal strip. The print tells you where the PMI module is. Inside...

7 years ago
Reply

That may work but you really want the generator running on true Neutral. I always set neutral when we get a generator back from the shop. You would be...

7 years ago
Reply

Ok, 908 makes more sense, more like I was thinking anyway. Do you have reduced stroke buffers with physical switches in the hoistway in addition to va...

7 years ago
Reply

You’ll get the 21 every time you put the car on inspection. The 26 fault says the drive is faulted and you don’t have drive ok. Do the 26 and 1801 fau...

7 years ago
Reply

If the LEDs light but you don’t see the input change state on the computer, the input board is bad, right?

7 years ago
Reply

This really sounds like a 14 & 15 contactors issue. Check, clean, or replace them, then adjust compounding.

7 years ago
Reply

If your 3 phase to the drive is good but the drive thinks it’s under volt, the drive has to go out. Not sure if others dive deeper into those drives b...

7 years ago
Reply

So you replaced PMI module 38 on PMI card #1? Did you check the Pico fuse for M38? That print doesn’t match your I/O map. Module 38 is P5-3 common, P5...

7 years ago
Reply

I 2nd that on checking the ripple. Especially if you are seeing the DC bounce around. After that, there is a plug in RAM card on one of the boards beh...

7 years ago
Reply

Of coarse like with any Miprom 21 going in the overhead with 38 errors you should do an NTS and ETS test to make sure they both work correctly. But if...

7 years ago
Reply

There is a software fix for this. Call Cetek and ask for target chasing software fix. This is only on AC drives, usually happens in the middle of the ...

7 years ago
Reply

I haven’t got a chance to try yet

7 years ago
Page 64 / 118