Reply

Not to the new model CPU. I figured it out this morning though, I had swapped XM13 and XH12 plugs when installing the CPU.

3 years ago
Reply

I have a book for the new drives right up to but not including the Ultra. Pretty similar though, then a startup routine that includes the Ultra

3 years ago
Topic
Replies: 3
Views: 2326
Reply

You need to find the LN card for the hall. Either in the controller or a box in the hoistway. If you have the 1085 SPI loop error the LED will be flas...

3 years ago
Reply

I’ve never paid attention to where the starter or logic board came from.

3 years ago
Reply

The most common reason for low oil shutdowns on any Dover equipment is a clogged up level strainer.

3 years ago
Reply

I have some stuff I’ll send you

3 years ago
Reply

Make sure you’re checking for faults in the door operator from the door IO and faults window. There isn’t a specific controller fault that tells you t...

3 years ago
Reply

If the OCSS status is going to NAV there should be a fault logged to go off of.

3 years ago
Reply

Ya, I always load the 2 copies of the job file and the 3 generic software files at the same time. Put all 5 in the same folder, select one in Hyperter...

3 years ago
Reply

So you can’t even see the job named folder? I’m not sure what’s going on there but I don’t think I’ve ever tried to load a job file like that before. ...

3 years ago
Reply

When you’re browsing for the file in Windows Explorer change the file type to all files

3 years ago
Reply

Relevel on stop switch is a parameter. Anti-creep.

3 years ago
Reply

CST is car stop switch

3 years ago
Reply

That should work. As an alternative to physical zone switches you could add discrete pi outputs and a relay for each floor in the controller. Of cours...

3 years ago