(@lowoil)
Reputable Member
Joined: 17 years ago
Posts: 270

   
Quote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635
 
How do you exit the “stuck” mode?
Car on IND?
Do calls cancel?
Stuck DOB?
Stuck PE? Try bypass button if provided. Or SE staying made?

Short of the above, you’ll need prints or someone who knows the numeric relay ID/function for call canceling or door open time.



   
ReplyQuote
(@lowoil)
Reputable Member
Joined: 17 years ago
Posts: 270
Topic starter  
I got it,idont know the numbers just 41 anf 29 had a bad door close limit.car would take all calls but sit with doors open after a run.



   
ReplyQuote
 Len
(@len)
Estimable Member
Joined: 17 years ago
Posts: 194
 
sounds like you are not dropping the 44 relay (Door Open)
status of STE relay up unless edge is tripped or stuck Door Open button
Door Open timer 70T..has a timed rc..Relay has to drop out ..delayed drop after door reaches fully open usually 3 to 8 seconds..adjustable.when doors reach fully open dol limit breaks.energizing DFO relay.



   
ReplyQuote
(@seco2000)
Eminent Member
Joined: 17 years ago
Posts: 27
 
IWestinghouse linear operator ? Check micro switches. OR Some had MAC operator... again check operator micro switches.