Looking for some help on a vertical express 2 stop hydro.... tried calling tech support for this and was told they won't help because we are not Thyssen techs.

During our recent state test during the fire service portion the inspector discovered a problem. Capture the car using the hall fire key, turn car on to phase 2 in the car and take it to the next floor up...all working good. When we turn the fire switch in the COP to the hold position it will not take calls and will sit with the doors open which is correct. The problem is that when on hold the door close button should be disabled however if you press it the doors will begin to close - it is constant pressure so if the switch is in the hold position and you press and hold the door close button the door will fully close. Once fully closed if you release the button the doors remain closed, if you press the open button the doors will not open. In other words on fire phase 2 with the key in the hold position, someone could theoretically walk into the car and hold the close button until the doors fully close and then would be trapped inside. as a result the elevator was shutdown and as i said a couple of attempts to get tech support on this have been useless. I believe this has been this way since original install since this inspector is a new guy and pretty thorough to say the least so in the past it has never been picked up. Thinking its a programming issue, all other functions of fire service work properly.

Hoping someone might have some insight on the issue, where and how to look/change any type of programming if needed or possibly send along a contact that is willing to troubleshoot this with us.

Thanks



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473
 
Assuming you have an ICON Controller, what is fire Service adjustment F16 set at?? If you are not in a state where there is some farout code deviation,IE Detroit, New York LA,etc., then it should be set at 13. The last number in the manual is 12, but there is a 13 and it is ANSI A17.1 2012 edition I think. You could also add a relay in the car station that is picked up when you go to hold and use NC contacts to open common to the door close buttons.
0=No Fire Service
1=Ansi-1993
2=Chicago Building Code
3=California
4=New York City RS18-1
5=Massachusetts
6=ANSI 1988
7=Houston
8=Michigan
9=B44
10=White Plains, NY
11=ANSI 2000
12=B44-2000



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473
 
I don't have a print handy, could it be wired to an incorrect input?/ I tried the fire service on a two stop today and door close does not allow the door close to function.



   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473

   
ReplyQuote
(@elevatorguy128)
Estimable Member
Joined: 17 years ago
Posts: 101
Topic starter  
appreciate all the responses.... im up in MA so our codes are little crazy. its an IMPACT controller. pic attached.
Attachments
23 norfolk.jpg (865.33 KB, 71 downloads)



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473
 
I would wire a relay to pick when you put the phase two switch in the hold position. Then use the contacts to disconnect the door close signal.



   
ReplyQuote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@ranger33)
Active Member
Joined: 17 years ago
Posts: 19
 
It looks like a Swift Meridia. There is a manual on Vertical Express website that looks similar to the CE/Swift ones.



   
ReplyQuote
(@jhessorz)
Trusted Member
Joined: 17 years ago
Posts: 46
 
I knew TK aquired CE but I didnt realize it was pre Futura. Worked on the 5000's, Meridias, and Futuras, but ive never seen one that looked like this. I remember them being Bluish Purple but everything , CPU , modules, and Contactors are all lined up exactly the same, is this still CE or is this a TK touch up?

Last edited by JHessorz; 03/14/20 02:15 PM.


   
ReplyQuote
(@miltronics)
Eminent Member
Joined: 17 years ago
Posts: 35
 
Please feel free to contact Issa Lwaysi from Miltronics Inc. @ (917) - 417 - 7389. We provide FREE Tech support for all CEC swift 5000, Futura, & Merida related equipment. 24/7 SUPPORT



   
ReplyQuote
(@elevatorguy128)
Estimable Member
Joined: 17 years ago
Posts: 101
Topic starter  
johnny, not sure of the input, will definitely check it. not familiar at all with this product and the prints were snagged before we got in.



   