(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635
 
What relays are in the MCD/MCE circuit? I think all eight at the lower right hand side of the main controller board. Are the relays a blue color? Problematic if so.



   
ReplyQuote
(@local-yocal)
Trusted Member
Joined: 17 years ago
Posts: 48
Topic starter  
yes they are blue. I seen on around page 12 what they are. All the valve pilot relays and muts. ordered all new relays for controller. will see if this takes care of it. if not i will replace cpu card



   
ReplyQuote
(@silly)
Estimable Member
Joined: 17 years ago
Posts: 215
 
Yeah the finder relays were garbage, started at like K-7 and worked its way up to 12? Before changing the CPU shout back. I might have a few more tricks up my sleeve by then, and I am assuming you check the battery by now.



   
ReplyQuote
(@street-rodder)
Eminent Member
Joined: 17 years ago
Posts: 25
 
Change all the relays at the bottom of the controller board, that's the
Problem. Use the Schrack, make sure you use the retaining clips too. ( very important)



   
ReplyQuote
(@local-yocal)
Trusted Member
Joined: 17 years ago
Posts: 48
Topic starter  
I changed all the finder relays for the schrack. Been running for over a week without out any shutdowns. It had to be reset at least once a day before the relay replacement. Think this may have did it. Thanks all for your input



   
ReplyQuote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635

   
ReplyQuote