Dover T4 (duplex 5 stops) trapping people intermittently, takes about 2 hours of running to warm up and create faults. 54, 56 and 628 faults. Car tries to run 3 times then needs a TFR
I have changed
1. MC and BK contractors along with their Aux.
2. C1 contactor and Aux. (below drive main contactor)
3. Changed BKO, BKI, BK2, BK3, MCI, GL, WDPF, GL, DRDY, DE Modules
4. All of the 120v ice cube relays above brake relays.

No clue where to go with this car has been off line for 2 months now. Customer getting frustrated as well as me.

Attachments
202469E4-83B8-49BD-80B9-66394C4DEF6B.png (517.32 KB, 51 downloads)
AEF04B6B-E181-4F9F-884B-C0F3C2F2154D.jpeg (630.46 KB, 45 downloads)
7BCFEF20-BC98-4DA3-9374-7126624DC984.jpeg (1.17 MB, 32 downloads)
71F119A4-2EE9-4535-B5AF-A4A8F474E561.jpeg (866.73 KB, 26 downloads)
27E6F6E3-B587-4F4F-AFC1-71E58522473B.jpeg (887.29 KB, 28 downloads)

Last edited by Dpless95; 01/13/21 02:22 AM.


   
Quote
(@master-of-none)
New Member
Joined: 17 years ago
Posts: 3
 
Had this same issue last week. Ended up being a bad IGBT. Make sure to use the heat sink compound when you replace it

Last edited by Master of none; 01/13/21 02:59 AM.


   
ReplyQuote
(@ray-oyler)
Active Member
Joined: 17 years ago
Posts: 5

   
ReplyQuote
(@ny-guy)
Trusted Member
Joined: 17 years ago
Posts: 82
 
Looks like these faults are leaning towards losing one of the power supplies that feed the drive. Check all the power supplies on the rear of the controller for voltage and AC noise. Most likely your problem.

Good luck!



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Looks like the 628 is the cause. I’ve never seen that one before though. How much AC voltage do you read in the bus? Could be the +/- 15v power supply, digital current regulator card, ribbon cable between DSP and current reg.



   
ReplyQuote
(@boomer)
Estimable Member
Joined: 17 years ago
Posts: 117

   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480

   
ReplyQuote
(@heisenberg)
Reputable Member
Joined: 17 years ago
Posts: 280

   
ReplyQuote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729

   
ReplyQuote
 TC7
(@tc7)
Trusted Member
Joined: 17 years ago
Posts: 71
 
I agree with jumping out voltage monitor especially if it is one of the orange ones. Possibly this is emergency stop from CPU shutting off very briefly. TKE had a bulletin to tap on the side of it with screwdriver handle to check for flaky internal connections/contacts. These have caused a great deal of aggravation. If that is your problem then replace the component. Also make sure you have good suppressors around contractor coils.



   
ReplyQuote
Share:
Scroll to Top