schindler 330A hall buttons

19 Posts
1 Users
0 Reactions
40.4 K Views
(@Vatorgator)
Joined: 1 second ago
Posts: 0
Topic starter   [#13599]
Have a duplex job that the mechanic is indicating trouble with only the top floor hall call. sometimes the hall light is on but no cars respond, he says he resets it and it will work, now he says that the button when pressed goes on then comes off, and nothing responds until he resets it. I'm not to familiar with this units hall call boards, sounds like a board problem to me, as all other floors are working is there any special programming involved in replacing this hall board, or is it just plug and play. any help is appreciated



   
Quote
(@JustWolf)
Joined: 1 second ago
Posts: 0
 
Plug and play, make sure rotary switch is in the corrct position and the plug jumper is removed from the botom of old board and placed on the new.



   
ReplyQuote
(@halfpick)
Joined: 1 second ago
Posts: 0
 
Using the SMLCD you should be getting error messages with extra info. It would appear that the board is failing.



   
ReplyQuote
(@justaguy)
Joined: 1 second ago
Posts: 0
 
once you see the button lit and unresponsive it's time to change the hall button pcb (hpbhna)...Schindler updated those boards due to so many issues and the new ones seem to be lasting a little longer...



   
ReplyQuote
(@vatormx)
Joined: 1 second ago
Posts: 0
 
Having a problem with top floor button as well. Reset boards, then replaced boards. The top button registers a call but light will not light. Someone recommended reducing the length of the CAT5 cables but doesn't seem logical if it has been working for 3 years with the same cables. Any thoughts? Programming? missing a jumper? Thanks,,



   
ReplyQuote
(@Vatorgator)
Joined: 1 second ago
Posts: 0
Topic starter  
forgot about this one, we replaced board, worked fine for about a week. then it went out all together, could not get it to work, so mechanic put the old board back in, and it has been fine ever since. over 4 months now go figure



   
ReplyQuote
(@NOTIME)
Joined: 1 second ago
Posts: 0
 
BIG "S" has problem with this board some elevator work greate some elevator must to remplace hall board weekly
they Circulate a Product Letter Recognizing the problem ant talk about a KIT but is not ready yet

some time just disconect the board and conect back and work for some weeks

Last edited by NOTIME; 08/14/16 10:56 PM.


   
ReplyQuote
(@Jcjphoenix)
Joined: 1 second ago
Posts: 0
 
We've had to replace many of these boards as well but cannot find anyone like world that will repair them. We've also been told by schindler that they are "throw aways" when they go bad. Has anyone found a place that will repair?



   
ReplyQuote
(@E-man)
Joined: 1 second ago
Posts: 0
 
Never had that many problems out of Hydro push button boards but the 400As? Gotta convert them to HFIs and make sure they are properly ground and the jumper configuration correct. Check the grounding.



   
ReplyQuote
(@shlomo)
Joined: 1 second ago
Posts: 0
 
hello to all of you,
does any one know if the drawings of schindler 3300 fit for schindler 5500,?
many thanks in advance



   
ReplyQuote
(@Sammy)
Joined: 1 second ago
Posts: 0
 
Had same problem with boards, the replacements came with documentation on grounding the cat 5 cable at the chripna board in the controller. I believe it was the cat 5 connecter beside the lift cat5 connector. It wasn't grounded when it was installed. If you order new boards from Schindler it should come with this info.



   
ReplyQuote
(@Smitty)
Joined: 1 second ago
Posts: 0
 
These boards are problematic but I have seen mechanical problems with certain fixtures. Make sure the actual button hardware is not binding the board or the connector.



   
ReplyQuote
(@Shadowman)
Joined: 1 second ago
Posts: 0
 
Originally Posted By: shlomo
hello to all of you,
does any one know if the drawings of schindler 3300 fit for schindler 5500

From what I've seen 5500 use a different controller. So one would assume it's different wiring for some parts. Other parts they would stick to the structure as the 3300. If you think about it, there's not much difference between a 3300 and a 5500 electrically. Only the inputs to the main controller would be different. The connections to the OKR would probably be the same. Good luck with your search.



   
ReplyQuote
 Amp
(@Amp)
Joined: 1 second ago
Posts: 0
 
we replace schindler hall call PCB i dont know ho to set the floor selection adress PCB has no any dip switch and rotry switch paleas help me out.



   
ReplyQuote
(@NOTIME)
Joined: 1 second ago
Posts: 0
 
in the Print, has a Hall Call page,that page say the config



   
ReplyQuote