Car generates a 2815 fault. During the cycle test it drops EES C and the DGR ((doorand gate)relay before allowing a run. The EES and C relays function fine and drop then repick as they should. The output CIO never toggles thus allowing DGR to stay picked.
I have been able to toggle the CIO output via the tool. The relays are in good shape and we did try a different EES relay with the same results.



   
Quote
(@smitty)
Reputable Member
Joined: 17 years ago
Posts: 220
Topic starter  
Sorry a quick correction.
The door gate relay is actually GDS.
This problem occurs on inspect as well as normal. The route mechanic did swap the LCMLB with a spare but the problem remained.



   
ReplyQuote
 Len
(@len)
Estimable Member
Joined: 17 years ago
Posts: 194
 
Do you know if this has the old mlb board..or has it been upgraded with the remote FUJI relays?

Last edited by Len; 06/10/14 01:50 AM.


   
ReplyQuote
(@smitty)
Reputable Member
Joined: 17 years ago
Posts: 220

   
ReplyQuote
(@smitty)
Reputable Member
Joined: 17 years ago
Posts: 220
Topic starter  
The problem turned out to be a faulty LCR contact. Another example of an error code leading one in the wrong direction.



   