Elevator Forum

Old Dover Door Issu...
 
Notifications
Clear all

Old Dover Door Issue

7 Posts
1 Users
0 Reactions
4,906 Views
(@wltr00)
Joined: 1 second ago
Posts: 0
Topic starter   [#25525]
Have an old relay logic Dover that as soon as you go to Auto the doors open. OD is not picked, SE is picked. There was vandalism to the doors including off the tracks, but have fixed all that, but this problem persists. Any help or suggestions would be appreciated.

Prints attached.

Attachments
Resized_20190102_150637.jpg (339.96 KB, 57 downloads)
Resized_20190102_145428.jpg (303.1 KB, 42 downloads)
Resized_20190102_145226.jpg (230.17 KB, 40 downloads)
Resized_20190102_150002.jpg (234.42 KB, 46 downloads)
Resized_20190102_150054.jpg (207.84 KB, 45 downloads)



   
Quote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
If the door opeerator circuit (line 329-339) is correct, there is a front and a rear door. Is this the case? OD will drop after the doors open and hit either Door Open Limit. Are you saying that the doors opened without DO, or that the doors opened when you put the mainline in? When SE falls, the doors should close.



   
ReplyQuote
(@wltr00)
Joined: 1 second ago
Posts: 0
Topic starter  
Yeah, the doors are opening without OD. And SE is staying picked.



   
ReplyQuote
(@danzeitz)
Joined: 1 second ago
Posts: 0
 
HAHA had this one before the orange capacitors across the door contacts are shorted!



   
ReplyQuote
(@john jay)
Joined: 1 second ago
Posts: 0
 
Danzeitz is correct. Had this one many times.



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
Wow, I have never seen front and rear door operators drawn together like that. It looks like the first one to get to DOL wins.



   
ReplyQuote
(@Johnny)
Joined: 1 second ago
Posts: 0
 
That was a first thought, but the print doesnt show any orange drop caps. I've worked for Dover distributors for 30 years and never saw one without them, but they were always on the prints.



   
ReplyQuote
Share: