1 1/16 away from DZ is normally pretty close. At the end of the learn run, your tool will display hoistway length and NRZ. I'll have to dig around, th...

10 years ago
Reply

When the learn run is complete, what value is displayed for NRZ? 20 is an ideal value.

10 years ago
Reply

I suspect that when your car is placed on inspection, you are losing door power. There is a parameter that allows you to either energize or de-energiz...

11 years ago
Reply

I think to clear PF RAM on a Gamma D the service tool command is 1-5-3 or 1-5-4, I know the command is not the same as a newer Otis unit. I have seen ...

11 years ago
Reply

S relay?

11 years ago
Reply

Check your tape magnets for slipping. A dab of RTV at the bottom of magnets keeps them in place.

11 years ago
Reply

Get the car at the recall landing with the doors open, turn the key in the hall station to reset and then off. PF ram reset is M-1-5-1.What type of Ge...

11 years ago
Reply

99% of the time if your problem is not an interlock, it is you your L3S limit switch. The car will leave the bottom floor and the switch will not make...

11 years ago
Topic
Replies: 2
Views: 3495
Reply

I agree. The gnp input needs to be GNP (active) not gnp (inactive).

11 years ago
Reply

Meter and print in the COP.

11 years ago
Reply

I'm guessing load weighing might be off and you get some roll back when the brake picks.

11 years ago
Reply

Good ideas. One man on the weekend would be rough. I've taken Saturday and Sunday before, 38 hours of OT...........

11 years ago
Topic
Replies: 8
Views: 10161
Reply

What is your access velocity set at? Let me look for some notes.

11 years ago