FYI, 8.6.4.6.2, states that if any adjustment is made to the Brake, that affects the holding capacity, you must test it. It also references 8.6.20.4, ...

7 years ago
Reply

Digital meters are too slow to catch a quick power glitch. Try a Triplett or a Simpson analog meter. When the contactor pulls in, you may be bouncing ...

7 years ago
Reply

Perhaps the ropes have stretched, and you are breaking a buffer switch.

7 years ago
Reply

You can probably drift it off the bottom final. Lift the brake, you may have to help it by prying on the brake pulley.

7 years ago
Reply

If this is part of a group, or a duplex you can look at those parameters. If you init the drive, you will lose all the field programmable parameters. ...

7 years ago
Reply

Check your brake springs. You should be able to move the washer under the springs. They should be finger movable.

7 years ago
Reply

do you have freight doors? If so does the cam retire?

7 years ago
Reply

I do believe the SIO find is a good one. But I also know after working on these,that there is still a software problem. When they first came out, they...

7 years ago
Reply

I agree, Brake failure is very possibly the culprit. The controller should have faulted, and set the brake.

7 years ago
Reply

Not familiar with the 2100 designation. Is this a standard 3 stop hydraulic, with inputs that are red, and outputs that are green? if so has anyone lo...

7 years ago
Reply

Very interesting. I will remember this one. Good find.

7 years ago
Reply

It is a software issue. Therefore nothing us mere mortals do will make it better. I know, I tried everything you did and more. I worked for this compa...

7 years ago
Reply

Cold oil, and a Dover valve. It happens a lot. Heat the oil and the problem will go away.

7 years ago
Reply

This was a software glitch that went on for years. It would happen I believe when the car was directed to park on another floor, because a different c...

7 years ago
Reply

Outputs should read to ss, as they are ground when in the on state. They should read 120 AC only. Inputs are 120 AC only, when referenced to L1A, or g...

7 years ago