We did find a melted resistor on both of the 72TC relays (see pics) and think this could be related to our issue considering it looks like a set of contacts off 72T control the 1 relay. We're troubleshooting with a set of Westinghouse motor generator prints, but this unit does not have an MG set. Wondering if anyone potentially has a better set of prints? Think i'm on the right track or any ideas? I'll definitely update when we figure it out!
The mechanic I was with claimed the retiring cam was pulling in when we pushed in a relay on the Peele door. We didn't actually verify from the car though.
Before I sent the car into the pit I could run the car up and down by pressing in either the number 1 or 2 relay. After releasing the down contactor one time, the car stopped, but then acted like it was trying to answer a floor call above it by going back up and then going into leveling on its own. It only did this one time though.
Another note of importance, the synchronous selector isn't moving in the controller. I don't see it listed anywhere on my set of prints.