VAC IN on the AC input modules, VDC IN on the DC input modules and VCC on both output modules

10 years ago
Reply

Can you see the MCA output change from 0 to 1? If so, can you pull the field wire from MCA where the thermal overload is or would be to see if MCAI go...

10 years ago
Reply

I think you mean PA3 board. You might check the ELI parameter under System > Adjust (Electronic Limit Interface). It should be set to 0 to use the ...

10 years ago
Reply

Nice work! Thanks for the update.

10 years ago
Reply

And these are wired like this:

10 years ago
Reply

I should warn you, these are not very exciting.

10 years ago
Reply

There are several of these used to pick relays. From a quick look at a TIV print these relays are all picked with an AC output module: S, BK2, BK3, CD...

10 years ago
Reply

Maybe but I did try it with a relay too. I did take a little video of all 4 variations working if you're interested.

10 years ago
Reply

Correction: the input module circuits should look like this. I wired up all 4 variations today. The input modules switch the - not the +. The DC outpu...

10 years ago
Reply

I would 2nd that. By a mile the most common cause of any up issues in an I-2 or I-3 valve. Always have a spare and clear O-Rings, replace the O-rings ...

10 years ago
Reply

There are no relay contacts in the valve coil circuit on a TAC32 and it monitors that there is voltage on the coil.

10 years ago
Reply

I ask because the 1043 is the standard low oil shutdown but I have had problems with the Z44 adjustment causing 1123 Up run stalled faults. Sticky pac...

10 years ago
Reply

What fault code specifically is it getting?

10 years ago
Reply

Inputs look right but I think the outputs should look more like this:

10 years ago
Reply
10 years ago