Otis overlay

4 Posts
2 Users
0 Reactions
4,676 Views
(@philelevman)
Trusted Member
Joined: 17 years ago
Posts: 42
Topic starter   [#18425]
I have a group of 4 1960s era otis with a small microprocessor overlay for fire service and dispatching and such. This is apparently the upgrade from the relay overlay. I have partial prints for the original, the relay logic mod and now a microprocessor mod. Im loosing my DO before the car gets into the floor so the doors do not open. I will try to post a pic if I can.



   
Quote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729
 
Make sure door reversal device is not firing cancelling door time. Some of the older stuff did not wait till door was open to cancel door time.



   
ReplyQuote
(@philelevman)
Trusted Member
Joined: 17 years ago
Posts: 42
Topic starter  
The DO ouput fires when in slowdown but drops before reaching the floor. The DO ouput pulls in the relay D1R and D2R aling with feeding the DZ brushes on the selector. Everything seems right until final slowdown then i loose my ouputs from the overlay



   
ReplyQuote