Notifications
Clear all
Topic starter
07/09/2017 6:44 pm
Job was shut down and constantly tripping breaker. Troubleshot it and found 220 vac breaker was bad. Replaced it. Then elevator would flash a2 until I made up locks and then it would run approx. 2-3 inches down and throw an E1 fault. Sent board to World for repair and when I wired it back up it is still doing same thing. The guy from Access states its bad green board. Also I have LEV run button and it is totally not functional on this unit only. Should I send board back again. Will IMS lead me towards problem.
07/09/2017 8:30 pm
check the L2 voltage, other than that the drive module is probably bad
08/09/2017 6:33 pm
I am now aware of IMS working on the LEV. If World repaired it for you, give them a call, or just send it back in. Access will help out, but they can not repair the boards, and will sell you the mod kit. World is who you should be calling as long as you have paid them money to repair.