Gen 2 mrl shutdown

20 Posts
9 Users
0 Reactions
30.9 K Views
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter   [#21535]
Hi guys. Got a gen 2 that's shut down.
Mcss shutdown codes are
2703
2811
2720

Mcss monitor status is
NRD SHD INA IDL

Ocss event log is
Cpu stack warn
Software reset
Proc exception
Mcss msg timeout
Mcss msg sio error
Ring 1 msg ck sum
Ring 1 msg sio error
Car was nav
Front dtc
Delay car prot
Spb com error
Rbi com fail
Spi bus error

Dbss log is
900 mcss timeout
913 mcss warning
000 power on
303 vac under
004 power down
304 vac imbalance.

I also saw traction loss on one of thf menu status screens.
Car will not run on inspection and the car is in the middle of shaft in between floors
What do u guys think ?



   
Quote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@intentec-luan)
Active Member
Joined: 17 years ago
Posts: 6
 
I think the MCSS board was bad,or fuse burned out.You can release the brake by one key turn on and press a red button on the little board.



   
ReplyQuote
(@elmcannic)
Honorable Member
Joined: 17 years ago
Posts: 635

   
ReplyQuote
(@tacotim)
New Member
Joined: 17 years ago
Posts: 2

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
Ocss car monitor is
A-** NAV M*

All fuses check out good. Unless I'm missing one sum where
I have no lights on safe 2, safe or gds
My ring 1,ring 2 , ocss, rsl, mcss, dbss, dcss lights are r blinking fast

My LD1 light is steady and LD2 is blinking fast and LD3 is blinking slow
Main line power checks out good and PSS power supply is green lit 24v

My mcss shutdowns are 2703 drive fault and 2956 PAL unsafe to run
2111 gateway fault , 2113 REM not configured 2720 ACP low ac trout(2720 not listed in fault paperwork write up)

My dbss log is
913 mcss warning
900 mcss timeout
304 VAC imbal
303 VAC under



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@dripcan)
Estimable Member
Joined: 17 years ago
Posts: 131

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
The controller is in the hoistway? WTF? What state are you in again? So what do you have to work with, just a Service Panel Board mounted in a jamb or something?

Thank god for the regulation state!



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
That is a damn shame. And I thought the MRL hydros with the controller in the jamb was a bad idea. (Those aren't legal here either). Is it at the top floor or bottom?



   
ReplyQuote