Tac 32. Pressure problem

15 Posts
7 Users
0 Reactions
16.8 K Views
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter   [#25049]
Hi guys. I got a tac 32 shutting down almost every morning with 2 faults
1110 - A17/B44 shutdown
1074 - jack low pressure shutdown

When this first happened I replaced the up leveling strainer and we had no problems for 10 days or so. Now it’s happening almost every morning. I adjusted the slow down on the valve body . But it is still shutting down.
Any ideas as to where to look next ?



   
Quote
(@lowoil)
Reputable Member
Joined: 17 years ago
Posts: 270
 
Make sure z44 is set to 100,did you turn in on the up slow down? An 1/8 or 1/16 turn in will stop those early morning stall outs.also check leveling speed after messing with up slow down .only seen this on brand new jobs dont remeber if it had the 1074 tho.



   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@solidstate)
Prominent Member
Joined: 17 years ago
Posts: 643

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@lowoil)
Reputable Member
Joined: 17 years ago
Posts: 270

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776

   
ReplyQuote
(@lowoil)
Reputable Member
Joined: 17 years ago
Posts: 270

   
ReplyQuote
(@xxxblazexxx)
Estimable Member
Joined: 17 years ago
Posts: 150
 
TAC 32 is 32 bit. Maybe you have old IMS. Its the Black Icon thats 32 bit. And does it happen to have telescoping jacks?



   
ReplyQuote
 Tata
(@tata)
New Member
Joined: 17 years ago
Posts: 1
 
Have problem with a tac32 hydro duplex . Only one car picks calls. The other has ebad light blinking. Could this be the problem ? What doesit mean.ITS MY FIRST TIME WITH THIS TYPE OF CONTROLLER



   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@jblack83)
Estimable Member
Joined: 17 years ago
Posts: 143

   
ReplyQuote
(@jluff)
Noble Member
Joined: 17 years ago
Posts: 776
Topic starter  
You may need to
Update your software I believe some older versions of the software have this low pressure problem but only during a jack resync. Do a FJR see what happens