Tac 32. Pressure problem

15 Posts
1 Users
0 Reactions
16.7 K Views
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter   [#25049]
Hi guys. I got a tac 32 shutting down almost every morning with 2 faults
1110 - A17/B44 shutdown
1074 - jack low pressure shutdown

When this first happened I replaced the up leveling strainer and we had no problems for 10 days or so. Now it’s happening almost every morning. I adjusted the slow down on the valve body . But it is still shutting down.
Any ideas as to where to look next ?



   
Quote
(@lowoil)
Joined: 1 second ago
Posts: 0
 
Make sure z44 is set to 100,did you turn in on the up slow down? An 1/8 or 1/16 turn in will stop those early morning stall outs.also check leveling speed after messing with up slow down .only seen this on brand new jobs dont remeber if it had the 1074 tho.



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
Thanks low oil. Can you tell me how to navigate on board to check z44



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
 
z44 would be the first thing. We had this issue not to long ago and posted on here. It was z44



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
How do I navigate to check and change z44?



   
ReplyQuote
(@solidstate)
Joined: 1 second ago
Posts: 0
 
You have to have IMS



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
I have ims for tac 20.



   
ReplyQuote
(@lowoil)
Joined: 1 second ago
Posts: 0
 
Should work i just plugged into a 32 and hit the 20 portion on ims and it works fine



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
It’s a different port and cable?



   
ReplyQuote
(@lowoil)
Joined: 1 second ago
Posts: 0
 
Jluff i sent u a pm



   
ReplyQuote
(@xxXBlazeXxx)
Joined: 1 second ago
Posts: 0
 
TAC 32 is 32 bit. Maybe you have old IMS. Its the Black Icon thats 32 bit. And does it happen to have telescoping jacks?



   
ReplyQuote
 Tata
(@Tata)
Joined: 1 second ago
Posts: 0
 
Have problem with a tac32 hydro duplex . Only one car picks calls. The other has ebad light blinking. Could this be the problem ? What doesit mean.ITS MY FIRST TIME WITH THIS TYPE OF CONTROLLER



   
ReplyQuote
(@Indirtwetrust)
Joined: 1 second ago
Posts: 0
 
That light means nothing on a hydro, not your problem.



   
ReplyQuote
(@Jblack83)
Joined: 1 second ago
Posts: 0
 
Constantly getting low jack pressure on some jobs. I will check the z44. Any result here?



   
ReplyQuote
(@Jluff)
Joined: 1 second ago
Posts: 0
Topic starter  
You may need to
Update your software I believe some older versions of the software have this low pressure problem but only during a jack resync. Do a FJR see what happens

Last edited by Jluff; 11/03/21 02:44 PM.


   
ReplyQuote