11/02/2025 12:53 am
I am having a issue with the door disconnect. When I change D-26 from a 1 to a 0, it just goes back to a 1. Before this happened, I had to replace the cpua for a separate problem. Any suggestions would be greatly appreciated.
11/02/2025 8:06 am
I can't recall for sure. But doesn't a 32 have a physical door cutout switch on the board? Maybe it's hit?
11/02/2025 8:17 am
Yeah it could be the DD switch. Work it a little. Maybe stuck or defective
09/03/2025 1:37 am
Was this after a new hoistway scan? Have you performed NTSD test at top and bottom? Generic software version 7B I think does not allow you to successfully complete an NTSD test so you would need to upgrade or downgrade, perform NTSD then change d26.
26/03/2025 7:37 am
Are changing d26 on ims? If so it should show a message. Like 420 said to learn ntsd or some other reason