Tac32 cpua replacement procedures

7 Posts
1 Users
0 Reactions
4,193 Views
 Jm21
(@Jm21)
Joined: 1 second ago
Posts: 0
Topic starter   [#38975]
Hello everyone
I'm looking for the procedures to replace the CPU a on a tac32 hydro. I just need the steps on how to download the job files and then upload them on the new CPUA. Any help is appreciated. Thank you

Last edited by Jm21; 02/11/25 02:19 AM.


   
Quote
(@wltr00)
Joined: 1 second ago
Posts: 0
 
Insert a blank USB memory stick into the USB slot on the CPUA board and enter UDLS in IMS Smart Fast. It show backing up software & then backup complete which will save the generic and job file to the stick. You can then connect the USB stick to a laptop. When it opens, open the TKE folder. Right click and create an update folder. Open the backup folder, and then open the job folder. Right click on the Generic and job file and select Copy. Open the update folder, right click and paste. Insert the memory stick into the replacement CPUA board. Press & hold Reset, then press & hold UDL. Let go off Reset while continuing to press and hold UDL until the LED flashes slow, slow, fast, fast and release UDL. When the upload is complete the controller will reset. Be sure to be on inspection while doing this.



   
ReplyQuote
 Jm21
(@Jm21)
Joined: 1 second ago
Posts: 0
Topic starter  
Thank you so much 👍



   
ReplyQuote
(@gohana256)
Joined: 1 second ago
Posts: 0

   
ReplyQuote
 Jm21
(@Jm21)
Joined: 1 second ago
Posts: 0
Topic starter  
Thanks gohana256, i see thats a cpuc and i have a cpua. Do you think its the same?



   
ReplyQuote
(@gohana256)
Joined: 1 second ago
Posts: 0
 
the procedure for backing up and reloading software are the same



   
ReplyQuote
(@Suthrn)
Joined: 1 second ago
Posts: 0
 
Becareful if you have a Tac32 Endura. Software may not work reloaded.



   
ReplyQuote