Elevator Forum

T1v need some help ...
 
Notifications
Clear all

T1v need some help please!!!

4 Posts
3 Users
0 Reactions
2,682 Views
(@hatedracing)
Active Member
Joined: 17 years ago
Posts: 4
Topic starter   [#21222]
So I have a t4 with an intermittent problem. It only happens maybe once a day. The car will take off for a split second to run and then fault with a 54 56 and 24 fault. I've traced it down to were I can recreate the problem by pulling the wire going to my wdpf module for a quick second. Same 3 faults will occur as if I'm dropping power to it real quick at the beginning of a run!!! I can't seem to find out where the 24vdc is coming from... the print shows it coming from a13-12 but I can't find that anywhere. If I leave the problem and let the car run as normal it does correct itself through sfr but if it happens at the top floor it rolls back right onto its final. I would greatly appreciate help with this problem.



   
Quote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@hatedracing)
Active Member
Joined: 17 years ago
Posts: 4

   
ReplyQuote
(@rolly)
Honorable Member
Joined: 17 years ago
Posts: 729

   
ReplyQuote