So,I have this Dover T3 and it goes down every once in awhile,usually a 87 and 12 fault.
That would be 87-brakeswitch and 12 something going wrong in the cartop selector.

My question is when I measure the voltage coming from the selector power supply,what should I measure?
I am measuring 15 volts,that is if I am measuring the place from the power supply.



   
Quote
(@johnny)
Honorable Member
Joined: 17 years ago
Posts: 473
 
12 is a parity error. Check placement of your BP magnets. you may want to swap PMI modules with another car and see if problem follows. Also look at your guides. They are critical. Rule of thumb--when front to back play exceeds 1 thickness of the selector tape, you should order and replace at next service visit. In a pinch, you can flip all left sides with the right sides and use the unused guides. The power supply is a 15vdc. 15.2 or 15.5 would be good. There is also 24V supplied to the selector for the outputs. You may have a line drop in voltage. I usually run my 24 volt supplies up as high as 26vdc, at the power supply, if possible. But this is your call.



   
ReplyQuote
(@elevatedone)
Estimable Member
Joined: 17 years ago
Posts: 132
Topic starter  
Thanks,man.
You are funny,service visit!
A call back is when I go to a unit.
All humor aside,wow,1 millimeter will cause problems.
The guides were flipped a few months ago,and they still look good,but a little wear.
Will replace on next callback.

Now,anyone got an answer to a Armour dynaglide problem?



   
ReplyQuote
(@broke-sheave)
Reputable Member
Joined: 17 years ago
Posts: 418
 
There is a life span on the PMI modules, and YES they do go intermittant...(Life Span was around 10 years)..

Change out all PMI's in the Reader box, and any others associated with it in the PMI boards upstairs.



   
ReplyQuote
(@elevatedone)
Estimable Member
Joined: 17 years ago
Posts: 132

   
ReplyQuote
(@elevatedone)
Estimable Member
Joined: 17 years ago
Posts: 132
Topic starter  
Still having shutdowns,almost daily now.
Main fault,Brake fault.

Replaced every pmi module,relay,brake switch, and what not.

I was running it on inspection from the MR today and about every 5 or 6 starts( I was running it a couple of feet at a time),the brake would pick,the motor would turn maybe slightly,the stop,then the brake would drop.When I press the down,or up button again,it would run.
No faults would show.



   
ReplyQuote
(@broke-sheave)
Reputable Member
Joined: 17 years ago
Posts: 418
 
Do you have a monitor in the machine room?

IF SO....

You can take a video camera, film the I/O's, and then walk off and leave it recording the I/O screen. You can then wade through all the video footage to the approximate time of the call back, and then slow the footage down to a few seconds before the fault occured. You can then see I/O responsible for fault.

Just a suggestion.



   
ReplyQuote
(@charlie)
Active Member
Joined: 17 years ago
Posts: 17

   
ReplyQuote
(@e-man)
Honorable Member
Joined: 17 years ago
Posts: 480
 
Have you done a brake job? When I've had 87s, it was either the BLS module, brake contact or the brake was sluggish and/or not adjusted correctly. I would also check all connections, contacts and voltages in the brake pick/hold circuit.

Last edited by E-man; 10/03/12 10:08 PM.


   
ReplyQuote
(@elevatedone)
Estimable Member
Joined: 17 years ago
Posts: 132
Topic starter  
Broke sheave,very good ideal.
I will bring it up with the super.

Charlie,I need to check into that as we have had several mechs working on this problem for at least 6 months or more,then it was dumped on me.

E-man,doing a brake job is my next step if I or someone else goes.
A little short handed ,so getting to it is an issue.
That part is out of my hands,I'm just a tech following orders.

It's an old geared montgomery machine with a brake virtually the same as what is used for dover composites.
It's a mod with a dc motor and generator.

BTW,thanks guys! Some info posted here has helped me with other issues on other units.



   
ReplyQuote
 E311
(@e311)
Reputable Member
Joined: 17 years ago
Posts: 363
 
If its a MECO geared machine check your brake pick and hold voltages. Most of these were 230vdc and a BUNCH of mod jobs that I have adjusted have had the brake supply topped out at 200vdc because the wrong power supply was ordered. These brakes can be very touchy if not properly adjusted and maintained.



   
ReplyQuote
(@elevatorman)
New Member
Joined: 17 years ago
Posts: 1
 
I had this very problem a few years ago. I ran the car a while before it occured. Only faulted when door preopened while stopping at a landing. It turned out to be a contact on the DZ relay. Replaced DZ1 & DZ2 relays. Good luck.



   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448

   
ReplyQuote
(@broke-sheave)
Reputable Member
Joined: 17 years ago
Posts: 418
 
Originally Posted By: sbrmilitia
Tear it out throw some swift in and fix all those problems.

T3 is basically a Swift 5000. True not a Futura or Meridia, but definitely it's predecessor.



   