Elevator Forum

Notifications
Clear all

Swift futura Hydro

14 Posts
5 Users
0 Reactions
20.9 K Views
 Len
(@len)
Estimable Member
Joined: 17 years ago
Posts: 194
Topic starter   [#9720]
I recently loss the dispatch on 1car in a 4 group system...all communication inputs and power supply voltage good...suspect either Spu board or Spu link board..any suggestions ...



   
Quote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
 
The SMIC board that plugs into the SMI board. Or the cable that links it. Does it says ##init or a 21 fault. If it is saying ##init type in the GET command and it should tell you why. if it says ok. Then SMIC board or cable is the problem.

Last edited by sbrmilitia; 02/04/14 03:41 AM.


   
ReplyQuote
 Len
(@len)
Estimable Member
Joined: 17 years ago
Posts: 194
Topic starter  
89 loss of dispatch flt...no other faults..swapped out spu link board with another car ...no change...will check grp parameters..



   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
 
how many cars are In the group. Which car are you using as the group car. Change the spu link on the car you use as your group. In one car you'll have a SMI card with you hall calls and other function modules change that SMIC board on that board.

Have you set up a frame capture so see if any of the SMIs turn red.



   
ReplyQuote
 Len
(@len)
Estimable Member
Joined: 17 years ago
Posts: 194
Topic starter  
Thanks for reply..we uploaded car parameters and ordered. New SPU board..spu link swap .....no change...



   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
 
SMIC board most likely a suspect. One of the controller will have a extra SMI board with the group and hall functions change that SMIC and try putting a new cable on it too. Also the RVU can cause this. There is one RVU board inside the white box you use to trouble shoot and also another RVU board in one of the controllers that handles the hall calls.



   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448

   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
 
Says a 89 fault for a hydro is this:

Dispatch sequencer clock interrupt failed. Detected by secondary watch dog timer.



   
ReplyQuote
(@smitty)
Reputable Member
Joined: 17 years ago
Posts: 220

   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448
 
GPO2 : Group Comm. handshake.
If ON, then this car is in the
Group

GPO1 : General purpose output. I think this is job specific so your prints should lead you in the right direction.



   
ReplyQuote
 Len
(@len)
Estimable Member
Joined: 17 years ago
Posts: 194

   
ReplyQuote
(@sbrmilitia)
Honorable Member
Joined: 17 years ago
Posts: 448

   
ReplyQuote
(@swift5000expert)
Active Member
Joined: 17 years ago
Posts: 18
 
I would check the nicad batteries on th spu board. The processor has multiple purpose comports and dispatch failes when nicads go bad.
I don't recomend swapping boards from other group or job numbers because you would have to flash the program to match the job numbers you are swapping to.
I had a bad batch of software and when I flashed the spu back to return to its normal group, I had an issue that took 3 months and a software change to correct. jferro@aceweb.com



   
ReplyQuote
(@miltronics)
Eminent Member
Joined: 17 years ago
Posts: 35
 
Please feel free to contact Issa Lwaysi from Miltronics Inc. @ (917) - 417 - 7389 with any service and support questions for all CEC products, SWIFT 5000, MERIDIA, & FUTURA. Miltronics Inc. fully supports all CEC products and we offer electronics repair services as well.



   
ReplyQuote
Share:
Scroll to Top