01/11/2017 3:28 am
Need some help here fellas. Can you communicate with a swift 5000 via hyperterminal and if so whats the proper procedure? Thanks.
01/11/2017 6:36 am
Yes, 1200, 8, N, 1.
Topic starter
01/11/2017 8:37 am
Got a 5000 tripping out with a 23, 24 flt only in the down direction, different spots in the h/w. Travel demand is 500fpm actual 497. DAR, REG Boards have been replaced with boards from running car in the same group. TAC & TAC cable have been replaced. Pwr supplies good with no AC ripple.Any ideas?
01/11/2017 11:56 am
which fault comes first?
Topic starter
01/11/2017 11:58 am
23
01/11/2017 7:20 pm
Magnetek drive? How close is your tach cable conduit run to high voltage wires? Are there big ass radio,microwave, cell tower, etc stuff on the roof of the machine room?
Topic starter
01/11/2017 7:39 pm
MG. I pulled a new tach cable outside of the piping and shortened it as much as I could. No tower interferences.
01/11/2017 8:50 pm
Check the SCRs
Topic starter
02/11/2017 9:33 am
Got it. I tweaked on the F pot on the DAR board. Been running with no faults for 8 hours. Thanks for all the help.