I have a 311 gem with a drive flashing !B1A
Also the fault on my service tool says precharge dc low
Can’t find what this means can someone help
Thanks



   
Quote
(@heisenberg)
Reputable Member
Joined: 17 years ago
Posts: 280

   
ReplyQuote
(@philly)
Reputable Member
Joined: 17 years ago
Posts: 256

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759
 
Most AC drives charge the DC buss through a resistance of some sort until it reaches a set voltage where the resistance is bypassed to fully charge the buss. Otis calls this precharge and once the parameter M1 pick V PU is reached, the M1 contactors in the drive picks to bypass the resistor and charge the buss all the way.



   
ReplyQuote
(@bytownvators)
New Member
Joined: 17 years ago
Posts: 1

   
ReplyQuote
(@indirtwetrust)
Noble Member
Joined: 17 years ago
Posts: 1759

   
ReplyQuote
(@bills)
Estimable Member
Joined: 17 years ago
Posts: 81

   
ReplyQuote
(@smitty)
Reputable Member
Joined: 17 years ago
Posts: 220
 
Access electronics out of Waldorf MD does a good job on these. I have replaced several of these over the years.
301 -645-1733



   
ReplyQuote
 efor
(@efor)
New Member
Joined: 17 years ago
Posts: 1
 
!B1A
i need your help to solve this problem
There are almost no parts left on the power floor that we haven't replaced, but the fault continues.



   